This is our first build out, and the contactor has been told that the new FSMA requirements are strict for RTE produce?, I have searched..reviewed any documentation I can find with regard to RTE processing requirements, and also spoken to a main preferred supplier, I can't get a definitive answer. Your advice on 99% filtration is excellent and helpful.
I will forward this on today at our weekly meeting.
Hi farm Mom,
I predict the first meeting question (and possibly from the Contractor also) will be 99% of what ?
I deduce you assess yr intended process area to be required to be sort of "High Care" capable in European Lingo.
Based on the few snippets attached below the consensus seems to be filter of grade F7 - H11 (hopefully intelligible to yr Contractor)
Post6 suggests a rather more efficient system than above but if cost permits, why not ?
PS - the detailed meaning of F7-H11 is in attachment in Post 2 of course
ven1 - Tesco ventilation high care.pdf 39.01KB
32 downloads
ven2 - BRC ventilation high risk.pdf 142.5KB
34 downloads
ven3 - ECFF ventilation high care.pdf 33.25KB
24 downloads
Edited by Charles.C, 11 January 2018 - 11:15 AM.
F11 > H11, sorry for typo