Best Answer Hoosiersmoker, 09 August 2022 - 06:19 PM
It depends on the fire codes in your state. Our code states they be no more than 75' traveling distance between FEs and there be one at every entrance. Signage needs to be placed in plain sight above each FE. Special circumstances or equipment would need to be separately considered. There also needs to be 36" clear access to them and they be protected. Never in the actual door opening itself as it is not protected there. Contact your state's DHS or Fire Marshall if it's different. Maybe just call your insurance company and they can direct you, if you have a good relationship with them